Default 12.0 DJC Intermittent Output Problem

Hi Gang,

I've got a problem with my DJC that I hope someone can help me with. Occasionally, it doesn't produce voltage. I encountered this problem when I first bought it, and thought it might be a defective field output circuit breaker. I installed a new one, and the generator worked fine. Today I tried it, and it wouldn't put out voltage. After poking around inside the regulator assembly, I tried it, and it worked fine. Two more tries and it worked fine, unloaded and loaded. I shut the unit down and tried it again. Alas, no output. It seems like if it starts and produces voltage, I don't have any problem. If it starts and doesn't produce voltage, I can shut it down and sometimes it will work on a restart, sometimes not. This has to be a simple problem like a loose connection, but I can't find it. The fact that it's intermittent makes it all the more fun. All of the terminal connections seem tight in the voltage regulator, and the foil on the circuit board looks good and clean.

The voltage regulator board is a #300-1540. When the unit is not working, the output is 36 VAC. When it is working, I can adjust the voltage pot on the regulator board and the output voltage responds smoothly. I was checking to see if there might be a dead spot on the pot. (ha-ha)

If anyone has encountered a problem similar to this, please let me know how you fixed it. Thanks in advance.

Steve
Reply With Quote
Sponsored Links
  #2  
Old 04-23-2005, 08:03:21 PM
Gunny Gunny is offline
Subscriber
 
Join Date: Feb 2005
Location: North Carolina
Posts: 3,835
Thanks: 1,856
Thanked 1,717 Times in 1,074 Posts
Default Re: 12.0 DJC Intermittent Output Problem

Steve:
Sounds like you do have residual voltage when it is not producing full rate output. Usually means the problem is not in the generator. Check all of the wires, especially F1 and F2, either that or you have a bad regulator. If you need one, PM me, don't pay Onan's price for a new one.
Reply With Quote
  #3  
Old 04-24-2005, 12:54:32 AM
Steve Dawkins Steve Dawkins is offline
Sponsor
 
Join Date: Feb 2005
Location: Virginia Beach, Virginia, USA
Posts: 1,178
Thanks: 881
Thanked 700 Times in 355 Posts
Default Re: 12.0 DJC Intermittent Output Problem

Thanks, Gunny. I'll go through the wiring again. This is a frustrating problem, since it is intermittent. Today, I was going through the troubleshooting flow chart in the YD service manual. I disconnected the CMR21 reactor to check continuity. The unit checked out and I connected it back to TB21. I started the unit before proceeding to the next step and it produced voltage. A couple of starts later, the output dropped to residual voltage again. GRRRRRRR! I'll keep your offer of the regulator board in mind.

Steve
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Onan 8k DKD Run Intermittent Problem OnanOmen Onan Generators 23 07-24-2019 11:00:15 PM
Briggs and Stratton Intermittent Problem EddyC Garden Tractors and Mowers 23 06-18-2019 12:58:30 AM
Onan 30.0ek-15r/23268m Intermittent Voltage Output Vwbugman00 Onan Generators 5 12-23-2017 08:11:19 PM
10CC61 Intermittent starting problem wa5dxp Kohler Generators 11 12-19-2013 07:37:09 AM
12.0 Onan intermittent output suthrnstyl2003 Onan Generators 35 08-20-2011 07:27:52 PM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 06:48:55 AM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2019 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277