  #1  
Old 06-14-2019, 12:56:56 PM
OldJalopy OldJalopy is offline
Registered-I
 
Join Date: Jan 2007
Location: Vallejo, California
Posts: 121
Thanks: 1
Thanked 15 Times in 12 Posts
Default Pressure Test the Boiler? Pressure Pump

What would be a good pump to hydro test the boiler?
Reply With Quote
Sponsored Links
  #2  
Old 06-14-2019, 01:51:19 PM
Jim Mackessy Jim Mackessy is offline
Subscriber
 
Join Date: Nov 2004
Location: Syracuse, New York, USA
Posts: 584
Thanks: 696
Thanked 512 Times in 245 Posts
Default Re: oressure test the boiler?Pressure pump

We use a McMaster-Carr 9108T2, about $350.00. No connection to the seller. Fill with water, prime, and then hook up to the boiler. There are better and worse out there. - JM
Reply With Quote
The Following User Says Thank You to Jim Mackessy For This Post:
  #3  
Old 06-14-2019, 02:00:55 PM
Odin Odin is offline
Subscriber
 
Join Date: Jun 2014
Location: Elmira, New York
Posts: 1,507
Thanks: 516
Thanked 1,250 Times in 645 Posts
Default Re: oressure test the boiler?Pressure pump

Have only done it on a boiler with a vintage hand pump that had little trouble getting the boiler up to test pressure after only a minute or two of vigorous pumping. Take care not to overshoot, you might hurt the boiler.

At work I have a nifty little air powered piston pump that was originally purchased for hydro testing gas field pressure vessels. It operates on 100 PSI compressed air, and was able to reach 600PSI test pressures on some large storage tanks being fabricated here years ago. Sadly we would later get burned by a bad partner and ended up getting out of the pressure vessel business, but I still have most of the test gear set aside. Might donate it to a club in NY that can put it to good use.
Reply With Quote
The Following 2 Users Say Thank You to Odin For This Post:
  #4  
Old 06-14-2019, 03:08:40 PM
OldJalopy OldJalopy is offline
Registered-I
 
Join Date: Jan 2007
Location: Vallejo, California
Posts: 121
Thanks: 1
Thanked 15 Times in 12 Posts
Default Re: Pressure Test the Boiler? Pressure Pump

Thanks guys, I don't really want to spend $350 just use one time, must be some other way.
Reply With Quote
  #5  
Old 06-14-2019, 03:45:48 PM
Power Power is offline
Registered-III
 
Join Date: Aug 2011
Location: New Jersey
Posts: 5,283
Thanks: 1,220
Thanked 3,162 Times in 1,859 Posts
Default Re: Pressure Test the Boiler? Pressure Pump

If boiler is small, you could try a small grease gun. piston is capable of very high pressures, but small displacement means a lot of pumping.
Reply With Quote
  #6  
Old 06-14-2019, 03:46:48 PM
oldtractors's Avatar
oldtractors oldtractors is offline
Subscriber
 
Join Date: Oct 2005
Location: Iowa Falls, Iowa, USA
Posts: 1,618
Thanks: 1,721
Thanked 1,903 Times in 776 Posts
Images: 5
Default Re: Pressure Test the Boiler? Pressure Pump

I built one from an old air cylinder and a couple of check valves. I probably have $25 in it not counting the hydraulic hose to attach to the boiler.
__________________
Jim Evans
Reply With Quote
The Following User Says Thank You to oldtractors For This Post:
  #7  
Old 06-14-2019, 03:50:58 PM
Jim Conte's Avatar
Jim Conte Jim Conte is offline
Sponsor
 
Join Date: Sep 2005
Location: Myerstown, Pennsylvania, USA
Posts: 1,762
Thanks: 3,428
Thanked 3,128 Times in 922 Posts
Images: 2
Default Re: Pressure Test the Boiler? Pressure Pump

If the boiler is completely full of water, a little bit of heat applied evenly will bring the pressure up . A rosebud or acetylene torch works fine. Do not use a power pump. It only takes a little water or heat to raise the pressure.
__________________
http://www.boilersaver.com/
Reply With Quote
The Following User Says Thank You to Jim Conte For This Post:
  #8  
Old 06-14-2019, 03:54:32 PM
Alan Rudd's Avatar
Alan Rudd Alan Rudd is offline
Registered-III
 
Join Date: Nov 2004
Location: Vero Beach, Florida USA
Posts: 581
Thanks: 4,679
Thanked 779 Times in 297 Posts
Images: 19
Default Re: Pressure Test the Boiler? Pressure Pump

What ever you do, do not hook up your pressure washer to use it for the source. You run the risk of rapidly over pressurizing and causing severe damage.

Alan
Reply With Quote
The Following 8 Users Say Thank You to Alan Rudd For This Post:
  #9  
Old 06-14-2019, 06:44:03 PM
Jim Mackessy Jim Mackessy is offline
Subscriber
 
Join Date: Nov 2004
Location: Syracuse, New York, USA
Posts: 584
Thanks: 696
Thanked 512 Times in 245 Posts
Default Re: Pressure Test the Boiler? Pressure Pump

What pressure are you trying for?
Reply With Quote
  #10  
Old 06-14-2019, 06:58:40 PM
OldJalopy OldJalopy is offline
Registered-I
 
Join Date: Jan 2007
Location: Vallejo, California
Posts: 121
Thanks: 1
Thanked 15 Times in 12 Posts
Default Re: Pressure Test the Boiler? Pressure Pump

Thanks Alan, I was just about to do just that. Probably 300# is all I need.
Reply With Quote
The Following User Says Thank You to OldJalopy For This Post:
  #11  
Old 06-14-2019, 08:06:03 PM
Mike McKnight Mike McKnight is offline
Registered-III
 
Join Date: Aug 2005
Location: Mason, Tennessee USA
Posts: 6,573
Thanks: 7,177
Thanked 6,605 Times in 2,420 Posts
Default Re: Pressure Test the Boiler? Pressure Pump

Ummmm, ain't no way I'd pump a 100 yr old boiler to 300# for a hydro test! Most states only ask to go either 1 1/4 x MAWP or at the very most 1 1/2!

Mike
Reply With Quote
The Following 5 Users Say Thank You to Mike McKnight For This Post:
  #12  
Old 06-14-2019, 11:27:55 PM
Odin Odin is offline
Subscriber
 
Join Date: Jun 2014
Location: Elmira, New York
Posts: 1,507
Thanks: 516
Thanked 1,250 Times in 645 Posts
Default Re: Pressure Test the Boiler? Pressure Pump

That has better be a locomotive boiler you are taking to 300 psi, and only after it has been inspected inside and out with ultrasound measurements taken.

Most of the steam traction I have seen is 150# or less, and as others have said would test to 1.25-1.5x mawp depending on your regional requirements.
Reply With Quote
  #13  
Old 06-14-2019, 11:37:08 PM
20 Reeves Highwheeler's Avatar
20 Reeves Highwheeler 20 Reeves Highwheeler is offline
Registered-III
 
Join Date: Aug 2005
Location: Helena, Montana USA
Posts: 8,139
Thanks: 9,514
Thanked 8,237 Times in 2,119 Posts
Images: 2716
Default Re: Pressure Test the Boiler? Pressure Pump

Quote:
Originally Posted by OldJalopy View Post
Thanks Alan, I was just about to do just that. Probably 300# is all I need.
At 300 psi, you're likely to hear a heavy "whump" inside the boiler. Maybe even outside? Like has been stated; 1.25 is good. Don't go over 1.5 of your MAWP. In the old days, many boilers had been ruined over a simple hydro. My opinion for what it cost... Gary
Reply With Quote
The Following 2 Users Say Thank You to 20 Reeves Highwheeler For This Post:
  #14  
Old 06-15-2019, 12:36:37 AM
Vanman Vanman is online now
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 5,898
Thanks: 9,493
Thanked 2,767 Times in 1,864 Posts
Default Re: Pressure Test the Boiler? Pressure Pump

Interesting. So, in some instances a boiler need only be tested to 1-1/4 times rated pressure?? That seems like a TINY safety margin!

So a mere 20% degradation or other minor change in conditions while under STEAM leaves you right on the threshold of BOOOOOOM!

I'd think something like a design safety margin of 4 times, and a test pressure of at least 2 times.

If I had a boiler bust open under hydrotest at double pressure I would be Grateful.

Now I realize that, for all these years, I have been perfectly well justified in my Boilerphobia.

Last edited by Vanman; 06-15-2019 at 12:35:37 PM.
Reply With Quote
  #15  
Old 06-15-2019, 01:46:17 AM
Power Power is offline
Registered-III
 
Join Date: Aug 2011
Location: New Jersey
Posts: 5,283
Thanks: 1,220
Thanked 3,162 Times in 1,859 Posts
Default Re: Pressure Test the Boiler? Pressure Pump

Quote:
Originally Posted by Vanman View Post
Interesting. So, in some instances a boiler need only be tested to 1-1/4 times rated pressure?? That seems like a TINY safety margin!

So a mere 20% degradation or other minor change in conditions leaves you right on the threshold of BOOOOOOM!

I'd think something like a design safety margin of 4 times, and a test pressure of at least 2 times.

If I had a boiler bust open under hydrotest at double pressure I would be Grateful.

Now I realize that, for all these years, I have been perfectly well justified in my Boilerphobia.
Vanman, Let me REALLY make your day. The safety margins are thinner than you may think! Boilers are hydro tested cold. 150 psi is about 365 degrees F. A 365 degrees F. operating temperature makes the 1 1/4 times MAWP cold hydro test a little less relevant.
Reply With Quote
The Following User Says Thank You to Power For This Post:
  #16  
Old 06-15-2019, 07:23:46 AM
DianneB DianneB is offline
Registered-I
 
Join Date: Aug 2012
Location: Manitoba, Canada
Posts: 274
Thanks: 4
Thanked 584 Times in 183 Posts
Default Re: Pressure Test the Boiler? Pressure Pump

I am notoriously CHEAP and when I needed a test pump, I picked up a pressure washer pump from a surplus outfit and fitted an adjustable pressure-relief valve and a 1/4HP electric motor. It worked well.
Reply With Quote
The Following 3 Users Say Thank You to DianneB For This Post:
  #17  
Old 06-15-2019, 07:31:35 AM
Jim Conte's Avatar
Jim Conte Jim Conte is offline
Sponsor
 
Join Date: Sep 2005
Location: Myerstown, Pennsylvania, USA
Posts: 1,762
Thanks: 3,428
Thanked 3,128 Times in 922 Posts
Images: 2
Default Re: Pressure Test the Boiler? Pressure Pump

Boiler go Boom on a hydro ?
Not hardly, Pilgrim.
That is the reason for using water, it is fairly in-compressible.
A little bit of a leak and the pressure is off.

It takes a large amount of Stored Energy to make an explosion.
ASME requires the water temperature to be between 70 and 120 F.

I know of some idiots, including contractors, who perform an air test at 1.5 X MAWP.
It is easy for them. They are either ignorant or uncaring.
They have set-up bombs and/or have a death wish.

The reason for the 70 - 120 F requirement ?
Cold steel can brittle fracture. We want our steel to be warm and tough.
If it is going to fail, we want it bending, not cracking.
__________________
http://www.boilersaver.com/
Reply With Quote
The Following User Says Thank You to Jim Conte For This Post:
  #18  
Old 06-15-2019, 08:52:36 AM
David Hoover David Hoover is offline
Subscriber
 
Join Date: Dec 2008
Location: Edmonton, Alberta, Canada
Posts: 1,550
Thanks: 2,186
Thanked 3,992 Times in 1,196 Posts
Default Re: Pressure Test the Boiler? Pressure Pump

Please don’t be offended Mr Jalopy, but there’s a lot of questions appearing and it would be awful for someone to get potentially hurt. Is their any experienced steam people in your area that could give you a hand? You’ve asked some very good questions but it may be time to have someone on sight who can oversee and stop anything bad that may be overlooked. It only takes one missed step to hurt you.
Reply With Quote
  #19  
Old 06-15-2019, 09:05:58 AM
OldJalopy OldJalopy is offline
Registered-I
 
Join Date: Jan 2007
Location: Vallejo, California
Posts: 121
Thanks: 1
Thanked 15 Times in 12 Posts
Default Re: Pressure Test the Boiler? Pressure Pump

Well, that got a lot of attention...............I was just guessing on the 300# figure. The old c 1921) steel boiler doesn't appear to be in too bad of shape, I gird-checked the inside shell and found everything over .250 but not real sure because of rust. I know the next thing is to hydro-test and guessed at 1 1/2 times original working pressure, which I also guessed at 150#, so OK make it 225#. Water is not going to blow up so I'm not worried about that, just wanted some ideas or source for a suitable pressure pump. Don't want to pump grease into the shell. I've asked a couple of men in my area to come by but they haven't had a chance to visit yet. I don't even know if the boiler is worth saving but I'll keep moving ahead, slowly....
Reply With Quote
  #20  
Old 06-15-2019, 09:34:36 AM
David Hoover David Hoover is offline
Subscriber
 
Join Date: Dec 2008
Location: Edmonton, Alberta, Canada
Posts: 1,550
Thanks: 2,186
Thanked 3,992 Times in 1,196 Posts
Default Re: Pressure Test the Boiler? Pressure Pump

Personally I’d stop at anything to do with pressurizing until someone is there to help, like you say your not yet sure if it’s even safe. Do all the looking and cleaning and investigating you want, but don’t pressurize it. You may at the least cause some unwanted strains that add to more repairs, or you could simply fuel over confidence that could lead to a bad experience. Do you belong to any clubs that offer steam schools? Have you any pics of your boiler to share?

Last edited by David Hoover; 06-15-2019 at 10:11:55 AM.
Reply With Quote
The Following 4 Users Say Thank You to David Hoover For This Post:
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
High Pressure Hydrostatic Test! G Willikers Steam Stationary Engines, Traction Engines 137 05-06-2015 10:05:14 PM
How do you test force feed lubricator pressure primerk5 Steam Stationary Engines, Traction Engines 8 05-08-2013 08:43:23 PM
pressure gage range versus working pressure chrsbrbnk Steam Stationary Engines, Traction Engines 8 04-30-2013 10:31:44 PM
Pressure is Pressure - An Injector WILL work if it's output goes into the steam space cyberbadger Steam Stationary Engines, Traction Engines 64 03-13-2013 04:19:47 PM
Why not test a boiler with air pressure? Dan Donaldson Steam Stationary Engines, Traction Engines 10 04-11-2006 07:15:48 AM


Use "Ctrl" mouse wheel to change screen size.