Finally got this genset to mess with after been sitting in the garage for a while, the problem was when i removed the starter relay few years back, i did not mark the terminals. I connected the starter relay to the b+ along with the other 3 terminals that would fit, and connected the other side to the genny along with the choke heating element. connect the small terminal(b+) to one side and the switch(b-) on the other, when i pushed the start switch, only the fuel pump and the coil is energized and no crank, but when i jump between the two big terminals, it will start fine as long as i press the start switch at the same time and i let go and will run ok. It will crank if I hot wire the small terminal with the b+ but will not start, I checked the voltage on the small terminal b+ and the voltage collapse to 0vdc when I press the start switch. Maybe I miss wired this unit?
Reply With Quote
Sponsored Links
  #2  
Old 01-12-2014, 11:59:07 PM
YellowLister YellowLister is offline
Subscriber
 
Join Date: Feb 2010
Location: Key Largo, Florida
Posts: 5,400
Thanks: 3,757
Thanked 3,486 Times in 1,999 Posts
Default Re: onan 6.5 nh 3cr/16000j

sounds like it. or one of your relays is backwards.. hard to say.. we need the full model and serial number and an email addressee and someone will send you a manual so you can see how its wired.
Reply With Quote
  #3  
Old 01-13-2014, 12:12:58 AM
John Ward John Ward is offline
Registered
 
Join Date: Jan 2012
Location: Chesterfield, Virginia, USA
Posts: 1,132
Thanks: 2,027
Thanked 812 Times in 475 Posts
Default Re: onan 6.5 nh 3cr/16000j

This should be in "Onan Generators", not in "Onan Craigslist" where genset for sale listing are posted.
Reply With Quote
  #4  
Old 01-13-2014, 12:37:34 AM
mongoose969 mongoose969 is offline
Registered
 
Join Date: Sep 2012
Location: Los Angeles, California
Posts: 13
Thanks: 0
Thanked 0 Times in 0 Posts
Default Re: onan 6.5 nh 3cr/16000j

sorry if this was posted at the wrong forum, the s/n is E773255564X and my email address is mongoose969@yahoo.com
thanks
Reply With Quote
  #5  
Old 01-14-2014, 12:02:01 AM
Kimbra Dean Kimbra Dean is offline
Subscriber
 
Join Date: Nov 2007
Location: Barnesville, Georgia, USA
Posts: 744
Thanks: 2,332
Thanked 380 Times in 269 Posts
Default Re: onan 6.5 nh 3cr/16000j

Use this link to download the UN generator manual.
http://www.cumminsonan.com/www/pdf/manuals/900-0196.pdf

Your wiring diagram is on page 6-15.

Do you have the correct solenoid. The solenoid for this generator is not the same as the one commonly seen on Ford cars and trucks from the late sixties / early seventies.

Some of the Onans used a solenoid with an isolated coil. The two ends of the solenoid coil are connected to the two small terminals. +12 volts is continuously supplied to one of the small terminals and the start switch grounds the other small terminal.

Others used a solenoid that has one end of the coil internally connected to the large B+ terminal. The start switch grounds the small "S" terminal that is connected to the other end of the solenoid coil.

The Ford Solenoid has one end of the coil grounded to the mounting bracket and requires +12 volts to the "S" terminal To start. A few Onan models use this Type solenoid but not yours.
Reply With Quote
  #6  
Old 01-14-2014, 12:10:15 AM
John Ward John Ward is offline
Registered
 
Join Date: Jan 2012
Location: Chesterfield, Virginia, USA
Posts: 1,132
Thanks: 2,027
Thanked 812 Times in 475 Posts
Default Re: onan 6.5 nh 3cr/16000j

Check your inbox...

M# 6.5 nh 3cr/16000j
S# E773255564

6.5kw
NH = model
3C = 120v or 120/240v re-connectable
R = remote start capable
16000 = options ordered
Spec letter = "J"
Built May 1977
Attached Thumbnails
Click image for larger version

Name:	6.5NH3cr16000J.jpg
Views:	39
Size:	232.1 KB
ID:	184879  
Reply With Quote
The Following 2 Users Say Thank You to John Ward For This Post:
  #7  
Old 01-15-2014, 11:02:59 AM
mongoose969 mongoose969 is offline
Registered
 
Join Date: Sep 2012
Location: Los Angeles, California
Posts: 13
Thanks: 0
Thanked 0 Times in 0 Posts
Default Re: onan 6.5 nh 3cr/16000j

thanks Kimbra and John for the info, yes the starter solenoid i used is the amc relay it has a floating ground. Finally got it wired correctly, the negative start switch and the wire from the relay connected together at the relay switch and the other small relay terminal is b+. thank you for all the help again, now i got 120/240vac at 61hz.
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Onan 3.2 HDZAA-6508B (aka Cummins-Onan RV QD3200) runs fine for ~3 minutes, then dies sajohnson Onan Generators 30 09-16-2019 07:09:47 PM
Onan 6.5NH 3CR/16000J Onan Dan Onan Generators 217 10-08-2018 09:23:33 PM
Onan 6.5 NI-3CR-16000J Can't get 240V out tprothma Onan Generators 11 10-17-2013 09:15:08 PM
NH 3CR 16000J replacing missing wiring harness Joe_Roach Onan Generators 2 09-27-2009 12:36:17 PM
Noob help with Onan 6.5 NH 3CR 16000J BigJayR Onan Generators 2 07-17-2006 06:01:30 PM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 10:42:49 AM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2019 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277